Outdoor unit incoming AC line supply overcurrent trip.
Troubleshooting guide for the York system fault F22.
Outdoor unit incoming AC line supply overcurrent trip.
Not sure which one it is — or if it's none of these? Try ACLogics today.
F22 trips when the outdoor unit's incoming AC line current exceeds the safe threshold monitored by the outdoor PCB — a whole-unit input-current protection rather than a component-specific one. This differs from F2, which reports overcurrent specifically at the compressor drive, and from F23, which is a single-phase overcurrent check within the compressor circuit; F22 is the broader AC-supply-side guard. When it trips, the outdoor unit shuts down compressor and fan operation, which cuts cooling/heating to all indoor units served by that outdoor unit.
Verify incoming line voltage and current draw against the unit's nameplate rating with a clamp meter. Check for a failing compressor, blocked condenser coil, or restricted airflow forcing the compressor to draw excess current. Inspect the outdoor PCB's current sensor/CT and wiring for damage or a bad connection. Confirm the outdoor unit isn't oversubscribed by too many indoor units or running with a dirty filter/coil across the system.